Harris FM 5K with a tube IPA. Still comparing the SS options. Any recommendations for A/C tonnage for this application? I've always been told that it's not good to oversize A/C capability, to prevent frequent compressor cycling.
And you plan on dumping the exhaust air into the room? The FM 5K is an old, rather inefficient transmitter, especially with a tube IPA. Converting this transmitter to a solid state IPA is possible, but probably a total PITA and wouldn't bring you much of a heat savings.
According to the original manual
http://gates-harris-history.com/manuals/fm/8881761012.pdf "2-9 Cooling Air Requirements" the transmitter needs a minimum air flow of 400CFM with a maximum intake temperature of 120 degrees F.
Assuming your transmitter building is 26' X 26', minimal roof/wall insulation, and containing heat-generating gear other than the transmitter, I'd estimate a minimum of 34,000 Btu's and 1,144.00 CFM of cooling would be required. 34,000 Btu would be around a minimum 3 tons of air conditioning. (2.86 to be exact)
Depending on the solid state transmitter, the number of Btu's required for adequate cooling would probably be about half. Caveat is: My estimate doesn't take into account for worst-case outdoor ambient temperatures, other equipment or uses in the building, humidity, etc.
For example, recently I did a similar calculation for a building in Baghdad Iraq. I ended up using a typical daytime summer month ambient air temperature of 130F. This drove up the air conditioning load by almost 40%. In other words, there is a lot to consider when designing cooling for a TX site, not just the transmitter.