1069_KIFR said:@ Scott, I really enjoyed your report on the SF visit. Although, I believe the photo identified as KGO's Old Home is actually the former home of KBHK TV 44. That was on Taylor Street. That does not look like the former home of KGO that was on Golden Gate Ave. Terrific job on the history of your transmitter sites and your visit.
Scott Fybush said:>>And, Steven, I suspect it's the non-halon stuff. That rack room was built post-halon, I'm pretty sure, and there's no way they'd use water there.
Engineer said:That looks like a conventional water sprinkler head to me - the odd object protruding down looks like an eyeball-type recessed light.
Gaseous fire suppression systems are somewhat rare in studio facilities -- even in rack rooms, it's extremely costly and space-consuming to house enough gas cylinders to cover the space. Not unheard of, but rare in my experience. They're more common in transmitter buildings - particularly high-dollar TV plants - because the buildings frequently don't have heating systems and there is the possibility of pipes freezing in areas that aren't kept warm by equipment. Typical systems today are FM-200 or Inergen. Existing Halon systems can stay in place but replacement Halon is very costly as no new gas can be made, it's all reclaimed and resold.
Pre-action is common in studio facilities. This system uses an air compressor to maintain air pressure in the sprinkler pipes and has an automatic valve keeping water out of the pipes. If some idiot hits a sprinkler head with a ladder, the system won't spray water everywhere and the loss of air pressure will provide a supervisory alarm. If two smoke/heat detectors go off in a zone, the system will charge the pipes with water, although that will still require the activation of a sprinkler head (melting of bimetallic element or glass tube) to discharge water.
Engineer said:That looks like a conventional water sprinkler head to me - the odd object protruding down looks like an eyeball-type recessed light.
Gaseous fire suppression systems are somewhat rare in studio facilities -- even in rack rooms, it's extremely costly and space-consuming to house enough gas cylinders to cover the space. Not unheard of, but rare in my experience. They're more common in transmitter buildings - particularly high-dollar TV plants - because the buildings frequently don't have heating systems and there is the possibility of pipes freezing in areas that aren't kept warm by equipment. Typical systems today are FM-200 or Inergen. Existing Halon systems can stay in place but replacement Halon is very costly as no new gas can be made, it's all reclaimed and resold.
Pre-action is common in studio facilities. This system uses an air compressor to maintain air pressure in the sprinkler pipes and has an automatic valve keeping water out of the pipes. If some idiot hits a sprinkler head with a ladder, the system won't spray water everywhere and the loss of air pressure will provide a supervisory alarm. If two smoke/heat detectors go off in a zone, the system will charge the pipes with water, although that will still require the activation of a sprinkler head (melting of bimetallic element or glass tube) to discharge water.
John Walker said:I'm surprised KNCI etc weren't moved into the Commerce Circle building. I've worked in both buildings, and Commerce Circle certainly has much more space than the Madison Ave bldg...not sure where they can fit all those Commerce stations in there