> > > A freind of mine just brought an outdoor TV antenna. The
>
> > > mast she is mounting it on comes from the ground up and
> > uses
> > > an eave mount to support it to the side of her house.
> She
> > > has the cable grounded but not the mast. Does she still
> > need
> > > to ground the mast(even though the mast sits in the
> > ground)?
> > >
> > >
> > > Thanks in advance
> > > DXER1
> > >
> > Hi,
> >
> > Ground the mast. 5' of buried mast is not a good ground.
>
> > The best way to do this is to locate the ground stake for
> > the building electrical entrance and run a #6 solid copper
>
> > wire from the stake to the mast and use approved
> connectors
> > on both ends. My local code requires a #6 wire or a
> conduit
> > protected #8. A stake at the mast may not be a good idea.
>
> > Good lightning protection is afforded by using a single
> > point ground to the electral entrance ground stake. Check
>
> > your local codes. Some require single point grounding.
> >
> > Neil
> >
> How long of a ground rod should she use? whould she use a 4
> ft. rod or go with an 8 ft. rod, or does that depend on
> local code as well? I said "me personally I would say use
> the 8 ft. rod so that you know that it is grounded. she aked
> me how would I ground the cable. I walked her through thoes
> steps as well. I just really needed advice and
> reccomendations/help on grounding the mast.
>
> Thanks again for the help and tips.
> DXER1
>
Hi again,
Subject to local codes, an 8 foot rod is the minimum to use. I still highly recommend single point grounding to the building electrical ground rod. I have a satellite dish on my roof, and a 2 meter stick on my chimney, each at opposite ends of my roof. I also have a coax fed dipole in the trees 60 feet behind my house. Both masts and the dipole shield are grounded to my electrical service ground stake with their own bare copper runs. I had a direct strike to a tree which is located at midpoint of the roof antennas and about 10 feet from the house. Half the tree was blown away indicating a big hit, but the only electrical damage I received was to the telephone system (lost three phones and a computer modem). I don't know if or where the bridge adapter for the line is grounded since I don't mess with phone company stuff. No damage whatsoever to the radio stuff which I do mess with. Also, no damage to the cable modem equipment. The cable company had bonded to the single point system next to the stake.
This experience, and what I have read on the subject makes me a believer in single point grounding. You might consult or hire an electrician to do this for your friend according to code. Then, as mentioned by one of the other posters, your friend will not only have good protection, but also a basis to argue denied claims from insurance.
Neil